Need some advice from those knowledgeable about Ontario Electrical Code.
Is it acceptable to connect a pony box to the main panel using 8 gauge stove cable. The cable is not jacketed in metal just the white plastic shielding that came with the cable.
Thanks,
Art
Drthorne
Nov 21st, 2007, 11:37 PM
yes, if it's protected by the right size of circuit breaker or fuse and the cable is not run through a wet location. 8 gauge would be a maximum 40amp breaker
sketchED
Nov 22nd, 2007, 02:06 AM
Sorry to highjack this thread, we recently purchashed a Built in Oven & a separate electrical cooktop, they will be going on top of one an other, however we only have one 40 amp outlet in the kitchen, (our old oven/burner was one piece)...can i connect both the cooktop and oven to the 40 amp electrical connection or do each of them need to be on separate fuses
fireguy9
Nov 22nd, 2007, 09:43 AM
Need some advice from those knowledgeable about Ontario Electrical Code.
Is it acceptable to connect a pony box to the main panel using 8 gauge stove cable. The cable is not jacketed in metal just the white plastic shielding that came with the cable.
Thanks,
Art
Thats fine
We have a pony panel for the pool and then another service panel for the addition coming off the main panel.
chrome_boy
Nov 22nd, 2007, 04:03 PM
Sorry to highjack this thread, we recently purchashed a Built in Oven & a separate electrical cooktop, they will be going on top of one an other, however we only have one 40 amp outlet in the kitchen, (our old oven/burner was one piece)...can i connect both the cooktop and oven to the 40 amp electrical connection or do each of them need to be on separate fuses
Check with the manual of the oven & cooktop. It'll tell you what it needs. I'm guessing you'll need separate circuits.