Humidifier Water Inlet Valve Not Flowing?

Hey guys,

My humidifier inlet valve/solenoid valve hasnt been flowing water for a few days. Dismantled the assembly and i have water going to the top of the valve but it does not pass through. Im thinking the obvious, valve is shot but is there another answer to this issue? Any help would be appreciated
Attached an image of it below

Image
Images
  • 20191117_203356.jpg
4 replies
Member
Jan 19, 2013
394 posts
220 upvotes
Ottawa
Have you verified it’s getting proper power?
Deal Fanatic
User avatar
May 1, 2003
6576 posts
250 upvotes
1chinaman wrote:
Nov 19th, 2019 10:58 am
Have you verified it’s getting proper power?
yes, check power first.

Also is your furnace running, heat on and blowing and humidity turned on high so the solenoid should be open?

Solenoid is cheap and easy enough to replace.
Deal Addict
Jun 16, 2009
1833 posts
517 upvotes
Woodbridge
Step 1 : Set furnace temp higher by 3 C so that it comes ON.
Step 2: Turn the dial of your humidistat to max.
Step 3: Do you hear click sound when furnace turns on and solenoid is energized? If Yes than it means you have power going to it but its not physically opening.
If you do not hear click sound :
Step A : Check the poer where yellow wires from your humidistat are connected ? If there is no power than check if you are getting power to the humidistat. If still the answer is no than check if the outgoing source is giving power at all ?
No power going to humidistat can be cuased by either faulty transformer or the terminal on board itself.


kammj1 wrote:
Nov 19th, 2019 10:21 am
Hey guys,

My humidifier inlet valve/solenoid valve hasnt been flowing water for a few days. Dismantled the assembly and i have water going to the top of the valve but it does not pass through. Im thinking the obvious, valve is shot but is there another answer to this issue? Any help would be appreciated
Attached an image of it below

Image
HVAC Professional. Committed to customer, not brand.
[OP]
Jr. Member
Nov 10, 2015
161 posts
112 upvotes
Thornhill, ON
bionicbadger wrote:
Nov 19th, 2019 11:24 am
yes, check power first.

Also is your furnace running, heat on and blowing and humidity turned on high so the solenoid should be open?

Solenoid is cheap and easy enough to replace.
newlyborn wrote:
Nov 19th, 2019 2:18 pm
Step 1 : Set furnace temp higher by 3 C so that it comes ON.
Step 2: Turn the dial of your humidistat to max.
Step 3: Do you hear click sound when furnace turns on and solenoid is energized? If Yes than it means you have power going to it but its not physically opening.
If you do not hear click sound :
Step A : Check the poer where yellow wires from your humidistat are connected ? If there is no power than check if you are getting power to the humidistat. If still the answer is no than check if the outgoing source is giving power at all ?
No power going to humidistat can be cuased by either faulty transformer or the terminal on board itself.


Thanks for all the answers. Got her running again woo!