BKDDC wrote:
Jan 27th, 2010 3:32 pm
all I can say is that we have very little issues therefore great value.more vinyl not always better. North Star uses a compound premium blend.most dont use this blend because of cost.what window do you sell.no air or expansion issues in over 20 years.
I don't sell any windows I am retired. I have built manufacturing equipment. done R & D, design and selling of windows, Aluminum clad, all wood, fiberglass and vinyl.

I can appreciate that you haven't had many issues in 20 years but that doesn't automatically mean that what you sell is the best. Also North Star has had a relatively recent redesign that has removed a lot of material from their windows.

You may not have had any complaints regarding air leakage, but the industry air infiltration tests prove that the North Star window leaks a lot more air that others. If you go to the Energy Star web site you can look this up.

http://www.oee.nrcan.gc.ca/residential/ ... cfm?attr=4

North Star = .48 L/S/M squared

Strassburger = .03 L/S/M squared

That's 16x s more air past a North Star window.

Add to this the greater expansion and contraction rate. The Strassburger window will win hands down in a comparison test.

Here are a few things to consider. North Star extrudes from a pellet. This means that the vinyl has already been extruded one time before it is extruded into the window profiles. The main problem with this method is that the additives are slightly evaporated during the second extrusion phase decreasing some of the properties of the vinyl. Many companies do this so that they don't have to store all the different additives, and have the mixing equipment. Another disadvantage is that the extruder (North Star for example) has lost control of the vinyl quality. The big advantage for them is that they only need to inventory the vinyl pellets.

Another thing is that the North Star window has been built with a narrower window sash than most of their competitors. This may offer a narrower mullion when the windows are joined, but the main benefit is for the ER numbers. More glass area means more solar heat gain which goes well with their Hard Coat Low E. The negative is that they are building a weaker window, and if you use U values the window will not perform nearly as well when tested with a soft coat low E
Newbie
Mar 1, 2005
83 posts
5 upvotes
Ottawa
I googled looking for a unit conversion tool since it appears not all entries on
nrcan use the same units.

Any idea of a good conversion tool for (m3/h/m) and (l/s/m2) ?
Newbie
Mar 22, 2008
18 posts
Could someone recommend a good Oran windows dealer/installer? I've come to the conclusion that their windows would give us the best ER value for windows with grills, but I have no idea where to get these windows. The numbers Oran gave to me lead to dealers for which I can find no further information - positive or negative.
Newbie
Jan 28, 2010
1 posts
Toronto
Cilucia wrote:
Jan 19th, 2010 1:02 pm
Image

My parents had new windows installed, but are really unhappy with the results. The new windows are smaller than the original windows, and there is a 1.5" gap around all the windows with 3-4 shims instead of 0-1. The contractor originally said the gap should be 0.5-1", but then backtracked with this when we complained:

[INDENT]3. Having a gap of 1.5” is not improper installation. If the gap is over 2”, then a build up should be used to reduce structural openings accordingly. In “new construction” the siding is installed after the windows, rough openings are created with a difference of 1” in height and width for shimming. Then the siding is installed afterwards. Retrofit installs are about fitting windows to openings, and in this case that is what we have done. Without the brickmould the windows would not be airtight and sealed against brick/siding. If we had ordered windows with the gap on the inside in mind you would have ended up with a messy caulking line and an aluminum cap on the exterior. We would have had a worse finished product in the end and then we would be talking about that instead of a gap that is not visible now.[/INDENT]

He said the windows are the maximum size they could have installed in our house... if they are the right size, why is there such a huge gap and 4 shims? His explanation makes no sense to me... /sigh. Can anyone chime in here?

We might have to take legal action. Any recommendations for someone who's experienced in disputes like this in the Ottawa area? Rona did the installation.

TIA
From CSA 440.4.7 Window installations
"6.4.2.2 Windows
Unless otherwise specifically required by the window manufacturer, the following clearances shall apply to
the installation of a window (except when installed into an existing frame):
(a) Except as provided for in Item (e), the width of the rough opening shall
(i) be between 19 mm (3/4 in) and 38 mm (1-1/2 in) greater than the width of the window frame;
and
(ii) provide a minimum gap of 9.5 mm (3/8 in) and a maximum gap of 19 mm (3/4 in) at each side
of the window. The window shall be centred in the rough opening such that the gap at each
side of the window is the same, i.e., ±3 mm (±1/8 in).
(b) Except as provided for in Items (c) and (e), the height of the rough opening shall
(i) be between 25 mm (1 in) and 44 mm (1-3/4 in) greater than the height of the window frame;
and
(ii) provide a minimum gap of 12.5 mm (1/2 in) and a maximum gap of 22 mm (7/8 in) at the top
and bottom of the window. The gap at the top of the window may be larger than the gap at
the bottom.
(c) In masonry veneer wood-frame walls, to allow for wall shrinkage, there shall be a
(i) 6 to 12 mm (1/4 to 1/2 in) clearance between the jamb and the masonry;
(ii) minimum 9.5 mm (3/8 in) clearance between the window sill and masonry sill on the first floor;
and
(iii) minimum 25 mm (1 in) clearance between the window sill and masonry sill on the second floor."


Shouldn't be any more than 2 shims thickness...
Newbie
Feb 20, 2008
19 posts
I just bought new windows from a company with high rating from HomeStars.com

There seems to be a lot of Condensation happening around all the windows in the house.

Could someone please let me know if this is normal?

I have the humidity let set to 20 on the furnace.
Newbie
User avatar
Dec 10, 2008
78 posts
8 upvotes
Hamilton
daku7 wrote:
Jan 31st, 2010 3:16 pm
I just bought new windows from a company with high rating from HomeStars.com

There seems to be a lot of Condensation happening around all the windows in the house.

Could someone please let me know if this is normal?

I have the humidity let set to 20 on the furnace.
This is something that does happen from time to time. If your existing windows didn't have condensation on them and leaked a lot of air and your new windows have been installed properly (brick to brick) then you have changed the conditions of your home by quite a lot. Since there is a lot less air leakage now the humidity in your home may possibly be increasing because there is not enough air leakage (something you can do manually by opening a window or 2 for a few minutes). Also the settings on your humidifier are only estimates, find out what settings work for different outside temperatures. Another thing that can be effecting this is the sudden cold snap we are having. It will now take your home longer to adjust to this as it is tighter.

If you had condensation before then it could be a number of things. To reduce condensation not only do you have to have the humidity levels low enough, you also have to have enough airflow. If the windows are covered by blinds, drapes, California shutters this can reduce airflow enough to cause condensation.

Windows never cause condensation as they don't produce water, they only show the conditions. The better the glass (u value, not ER) the higher the humidity you can have before condensation occurs ( soft coat low E is better than hard coat as it has a higher U value). The other factor which can effect the windows resistance to condensation is the type of spacer being used. Non metallic spacers are warmer than metallic ones, which spacer is best all around is another conversation.

There are so many things that can cause and cure this you should have the company that sold you the windows come by and help better explain this as to your homes conditions. Each home is different. It would be best to try and have them come by when the condensation is happening, and to leave the house in the same condition, window covering open or closed etc.
Newbie
User avatar
Dec 10, 2008
78 posts
8 upvotes
Hamilton
vinylwindows wrote:
Jan 29th, 2010 11:50 pm
From CSA 440.4.7 Window installations
"6.4.2.2 Windows
Unless otherwise specifically required by the window manufacturer, the following clearances shall apply to
the installation of a window (except when installed into an existing frame):
(a) Except as provided for in Item (e), the width of the rough opening shall
(i) be between 19 mm (3/4 in) and 38 mm (1-1/2 in) greater than the width of the window frame;
and
(ii) provide a minimum gap of 9.5 mm (3/8 in) and a maximum gap of 19 mm (3/4 in) at each side
of the window. The window shall be centred in the rough opening such that the gap at each
side of the window is the same, i.e., ±3 mm (±1/8 in).
(b) Except as provided for in Items (c) and (e), the height of the rough opening shall
(i) be between 25 mm (1 in) and 44 mm (1-3/4 in) greater than the height of the window frame;
and
(ii) provide a minimum gap of 12.5 mm (1/2 in) and a maximum gap of 22 mm (7/8 in) at the top
and bottom of the window. The gap at the top of the window may be larger than the gap at
the bottom.
(c) In masonry veneer wood-frame walls, to allow for wall shrinkage, there shall be a
(i) 6 to 12 mm (1/4 to 1/2 in) clearance between the jamb and the masonry;
(ii) minimum 9.5 mm (3/8 in) clearance between the window sill and masonry sill on the first floor;
and
(iii) minimum 25 mm (1 in) clearance between the window sill and masonry sill on the second floor."


Shouldn't be any more than 2 shims thickness...
In a perfect world this is correct and should be followed when building a new home.

Unfortunately this cannot always be followed in a replacement situation. No one has X ray eyes to see what's in the wall of an existing home, and not to many customers want all their casings removed for installers to look at each and every gap, and then wait for 4-12 weeks for the new windows. Also the minimum clearance of 1" below a second floor window sill and the masonry sill is not needed as the house will have already shrunk. A smaller gap of 1/4" - 3/8" is more than enough.
Newbie
Dec 20, 2009
11 posts
vernon bc
We've finally narrowed it down to either Gienow windows or Euroclad Building systems (they use PH Tech extrusions). Can someone give some advice on the quality of both and which one they would chose and why. I've tried to look up the CSA ratings on both, but for some reason they aren't listed. Is there another way to check this without going to that specific website? Both companies say the windows have been CSA A440 tested so i don't know why i'm having trouble with this :confused:
Thanks in advance for responding. This forum has been really great for my research. The guy at Gienow couldn't believe how much I knew!!
Newbie
User avatar
Oct 3, 2008
73 posts
2 upvotes
I don't see Euroclad on the Energy star site, and neither one of them on the CSA listings. One of the reasons I suspect this being the case is because PH tech had their system tested and Euroclad buys the system off of them and use that excuse.This happens quite frequently in this business. Smaller companies(and I'm not saying Euroclad is) will not have the finances to test their own product. Even though I like the PH tech extrusion I would probably trust someone who has tested the products themselves and stick with Gienow
Newbie
Dec 20, 2009
11 posts
vernon bc
So Windowexpert,

If a product has the best vinyl (ph tech) and the best glass (cardinal), wouldn't that automatically make it a better product than a builder entry window? We are having a euroclad rep come to the house along with our builder. Can you suggest some important questions I might ask? ALso, in a previous email, you were right in saying that their ratings are piggybacked on ph tech. He states that they will have energy star in a month or so. Is there a way for me to verify this?

Again, any information is greatly appreciated!
Newbie
User avatar
Oct 3, 2008
73 posts
2 upvotes
this may very well be the case that they will have all the tests done in a month because it does take a while. On the other hand it can easily be a sales pitch. If they are getting the results in a month then ask him what the ratings are... surely the company will know them even though they are not posted on their site.
Your theory about using the best vinyl and the best glass? That's a tough question first of all there are alot more parts than just glass and vinyl. If I went to the Mercedes dealership and bought all the parts to make my new car I doubt it would turn out as good as the ones coming from a state of the art plant in Germany
Newbie
Dec 20, 2009
11 posts
vernon bc
I did get the CSA results from euroclad, but not the energy star U factor, SHGC, and ER.

They are as follows:
Casements: A3 B7 C5 F20
Fixed/Picture: B7 C5 (note:no air filtration or fixed entry rating as fixed)
Patio Slider: A3 B4 C3 F5

To compare with Gienow
Casements: A3 B7 C5 U-1.10 SHGC .16 ER 25
Fixed/Picture: B7 C4 U-.95 SHGC .20 ER 31
Patio Slider A3 B2 C3 no data

So I guess I should be asking how they put their product together? etc. Could you tell me what specific things I might look for when the euroclad rep comes. Or things to be weary of?
Newbie
User avatar
Oct 3, 2008
73 posts
2 upvotes
ask them what hardware they use. Some are made in China and some is made in Canada/US. Do they wet glaze or dry glaze, in other words do they use silicone or some kind of caulking when they are inserting the glass. Who is their glass supplier or do they make their own glass units. Cardinal is the manufacturer of glass but if they use 30 year old equipment to put it together chances are you will have problems. Ask if you can see their manufacturing facility, if it's a solid company they will probably let you have some kind peek at it. I suspect they are a smaller operation who buys their extrusion, glass and everything else and slaps it together, depending on their welding machinery even with the PH tech extrusion those welds can come apart fairly quickly. Warranty is another good one: we always knock Home Depots and Rona's of this world but their exchange policies are great, I think we have all returned something there at one point or another, the smaller guys just want your $$$ and run
Newbie
Dec 20, 2009
11 posts
vernon bc
This is great information. Thanks again for taking the time to write. I'll post an update after our meeting with Euroclad. In your opinion, is dry or wet glazing better?
Newbie
Jan 11, 2010
18 posts
toronto
windowexpert wrote:
Feb 2nd, 2010 7:38 am
I don't see Euroclad on the Energy star site, and neither one of them on the CSA listings. One of the reasons I suspect this being the case is because PH tech had their system tested and Euroclad buys the system off of them and use that excuse.This happens quite frequently in this business. Smaller companies(and I'm not saying Euroclad is) will not have the finances to test their own product. Even though I like the PH tech extrusion I would probably trust someone who has tested the products themselves and stick with Gienow
I dont know much about the other guy, but I have visited Gienow in Calgary... they have an impressive operation and they are very quality oriented. I would say comparable to the andersens and pellas.

P.S - i hope you dont beleive that cardinal has the best glass or even insulating glass.
× < >

Top