8Amp corded mower trips 15Amp rated circuit breaker

I am using a 8Amp corded mower (with an extension cord) and it runs well most of the time. When I hit a thick patch of grass that is hard to cut, the circuit breaker trips. I checked the circuit breaker (in the basement) and the outlet I plugged the mower into is rated 15Amp (in fact all breakers are rated 15Amp or higher). I'm in GTA, Ontario.

Why does an 8Amp corded mower able to trip a 15Amp rated circuit breaker? Does the harder to mow areas cause the mower to draw more amps?

I'm planning on replacing this 8Amp corded mower with a 12Amp corded mower but this circuit breaker causes me concern. Would the 12Amp corded mower be able to not trip 15Amp circuit breaker, even in hard to mow areas? Or will the 12Amp corded mower more frequently trip the 15Amp circuit breaker?
24 replies
Deal Expert
May 30, 2005
48247 posts
9136 upvotes
Richmond Hill
There are many reasons:
- Your mower being rated at 8A usually means there is a resistive circuit to bring down the maximum current to 8A. This circuit could be faulty
- Your breaker is rated at 15A but that doesn't mean it trips whenever you go past 15A - depending on the type of breaker, it could trip lower. Breakers also age over time and need to be replaced

Ultimately the only way you can tell for certain is to use something like a Kill-A-Watt while going over that patch of grass. If you are not a frequent mower, mow high once, then switch to a lower setting.
Deal Expert
User avatar
Feb 11, 2007
20287 posts
24036 upvotes
GTA
My 12A mower doesn't trip my 15A circuit. Is there anything else running on that circuit?
Have you tried plugging it into another circuit? You could have a faulty breaker.
If the women don't find you handsome, they should at least find you handy.
Deal Fanatic
User avatar
Jun 21, 2003
5985 posts
3408 upvotes
Stoney Creek, ON
Is the Breaker an arc fault breaker? If so and your mower is old you could have arcing on the motor brushes that is causing the trip.
Deal Addict
User avatar
Dec 12, 2006
4354 posts
578 upvotes
Messed Up Area
Also your extension cord could be causing problems if too long or and to high of gauge. Also if ground pins are missing.
Deal Fanatic
User avatar
Oct 19, 2008
7340 posts
2929 upvotes
Whitby
theguyz wrote: Also your extension cord could be causing problems if too long or and to high of gauge. Also if ground pins are missing.
Yep, bet he's using a 16 or even 18 gauge long extension cord. Blades need sharpening, long grass, crap extension cord = circuit breaker tripping.
Deal Expert
May 30, 2005
48247 posts
9136 upvotes
Richmond Hill
Zamboni wrote: Yep, bet he's using a 16 or even 18 gauge long extension cord. Blades need sharpening, long grass, crap extension cord = circuit breaker tripping.
Assuming the mower was designed and functioning properly, though, the motor should just stall instead of pulling more than 8A (what it was rated for)
Deal Fanatic
User avatar
Oct 19, 2008
7340 posts
2929 upvotes
Whitby
Jon Lai wrote: Assuming the mower was designed and functioning properly, though, the motor should just stall instead of pulling more than 8A (what it was rated for)
Its not drawing more than 8amps....its not getting the 8amps because of voltage drop IF he is using 16 gauge extension cord. I don't think 16 gauge extension quite carries 8amps even at short length, so when the motor is taxed it trips the breaker. Probably runs hot also if its a 50' cord.
Deal Addict
User avatar
Oct 2, 2018
2627 posts
3112 upvotes
Toronto
Could be an aged partially defective breaker as well. Personally i would pick up the new 12A mower like you want and things will be fine, if a problem persists i would replace the breaker or at least swap the breaker to another one in the panel as that should eliminate the breaker from the issue. Check to make sure you don't have another load on the circuit that you are unaware of like a small fridge or similar.

I'd put my money on just an old run down mower where the motor is drawing too much under load or a bad breaker.
“Laughter is timeless, imagination has no age.....and dreams are forever.”
Deal Addict
May 16, 2017
2542 posts
3366 upvotes
Sure wouldn't rely on this thread for electrical knowledge.

Long cord with resistance that REDUCES voltage AND current will not trip the breaker at 8A load. Amps at both ends of the cord are the same - a matter of physics.

There will NOT be a resistive limiter to make an 8A rated electric motor that would otherwise be 15A rated.

Many electric motors can and will draw more than their rated current if the motor RPM is slowed by heavy load.

Is there another load on this circuit that isn't identified? Old/worn breaker is possible. Or the mower motor has some sort of fault in the winding drawing extra current.
Deal Expert
User avatar
Jun 12, 2007
19630 posts
6376 upvotes
London
Outside? - GFI breaker or receptacle might be bad or just too sensitive
Test by plugging into an inside outlet
Deal Expert
Jan 27, 2006
21157 posts
14702 upvotes
Vancouver, BC
What you are seeing is actually expected.

Electric motors have two current ratings (more if you want to look at current graphs and different situations but that's another discussion) - free current and stall current. Free current is the standard number people see when the motor is running freely (ie no extra resistance and running at the rated RPM). Stall current is just what it sounds like... when the motor is under heavy load and is stalling. The motor uses more power to try to move when stalled or stalling than when the motor is free running.

In your case, the 8A rating is probably based on free current - ie the lawnmower consumes 8A of current when the motor is running freely at the operational RPM. When your lawnmower hits a rough/thick patch of grass, the motor loses speed and starts to stall which will increase the current draw. If the rough/thick patch is small, the higher current draw is short as the motor recovers quickly. However, if the rough/thick patch is larger, the higher current draw is much longer as the motor's speed can't recover causing a prolonged higher current draw that may trip the breaker.
Deal Fanatic
User avatar
Jun 21, 2003
5985 posts
3408 upvotes
Stoney Creek, ON
robsaw wrote: Sure wouldn't rely on this thread for electrical knowledge.

Long cord with resistance that REDUCES voltage AND current will not trip the breaker at 8A load. Amps at both ends of the cord are the same - a matter of physics.

There will NOT be a resistive limiter to make an 8A rated electric motor that would otherwise be 15A rated.

Many electric motors can and will draw more than their rated current if the motor RPM is slowed by heavy load.

Is there another load on this circuit that isn't identified? Old/worn breaker is possible. Or the mower motor has some sort of fault in the winding drawing extra current.
The long cord won't REDUCE voltage AND current. It will create a voltage drop which will result in increased current as the motor will pull more current to compensate for the lower voltage in attempting to maintain it's rated RPM. I agree that on an 8A load it probably won't trip the breaker alone but it could if combined with any other issue.

But until OP returns with more information we'll never know what the problem is.
Sr. Member
Oct 2, 2017
850 posts
604 upvotes
Extension cords cause a high number of fires.. if the breaker is tripping the cord is bad and you should replace it.
I'll see you at the top, cause the bottom is too crowded
[OP]
Deal Addict
Oct 22, 2014
4694 posts
3003 upvotes
Toronto
Zamboni wrote: Its not drawing more than 8amps....its not getting the 8amps because of voltage drop IF he is using 16 gauge extension cord. I don't think 16 gauge extension quite carries 8amps even at short length, so when the motor is taxed it trips the breaker. Probably runs hot also if its a 50' cord.
robsaw wrote: Sure wouldn't rely on this thread for electrical knowledge.

Long cord with resistance that REDUCES voltage AND current will not trip the breaker at 8A load. Amps at both ends of the cord are the same - a matter of physics.

There will NOT be a resistive limiter to make an 8A rated electric motor that would otherwise be 15A rated.

Many electric motors can and will draw more than their rated current if the motor RPM is slowed by heavy load.

Is there another load on this circuit that isn't identified? Old/worn breaker is possible. Or the mower motor has some sort of fault in the winding drawing extra current.
ChicoQuente wrote: The long cord won't REDUCE voltage AND current. It will create a voltage drop which will result in increased current as the motor will pull more current to compensate for the lower voltage in attempting to maintain it's rated RPM. I agree that on an 8A load it probably won't trip the breaker alone but it could if combined with any other issue.

But until OP returns with more information we'll never know what the problem is.
Thanks for your replies. There is no other load on this outlet, just the mower. I observed the breaker tripping on a separate outlet (also has 15A breaker) , with no other load.

The extension cord I used is 14 gauge (15 amp x 125v) and 50 foot long. Is the extension cord's length that is increasing the amperage drawn or the extension cord's gauge? I have another 16 gauge extension cord (13A x 125V) 50 footer, which is noticeably thinner, should I use that instead?

I don't understand what is the impact of the extension cord gauge, except the smaller the gauge number the safer (able to hold more current/amperage).
Last edited by Elfwood on Jul 4th, 2021 11:33 am, edited 4 times in total.
[OP]
Deal Addict
Oct 22, 2014
4694 posts
3003 upvotes
Toronto
craftsman wrote: What you are seeing is actually expected.

Electric motors have two current ratings (more if you want to look at current graphs and different situations but that's another discussion) - free current and stall current. Free current is the standard number people see when the motor is running freely (ie no extra resistance and running at the rated RPM). Stall current is just what it sounds like... when the motor is under heavy load and is stalling. The motor uses more power to try to move when stalled or stalling than when the motor is free running.

In your case, the 8A rating is probably based on free current - ie the lawnmower consumes 8A of current when the motor is running freely at the operational RPM. When your lawnmower hits a rough/thick patch of grass, the motor loses speed and starts to stall which will increase the current draw. If the rough/thick patch is small, the higher current draw is short as the motor recovers quickly. However, if the rough/thick patch is larger, the higher current draw is much longer as the motor's speed can't recover causing a prolonged higher current draw that may trip the breaker.
Thanks. Yes that fits my observation of when the mower trips the breaker. So if I purchase a 12A mower, will it trip even more frequently (on rough/thick patches) since it's closer to the breaker's limit of 15A? Or is the 12A mower more powerful and able to push through the rough/thick patches on free current (without stalling)?
Deal Addict
Jun 14, 2008
4353 posts
3210 upvotes
Montreal
Elfwood wrote: Thanks. Yes that fits my observation of when the mower trips the breaker. So if I purchase a 12A mower, will it trip even more frequently (on rough/thick patches) since it's closer to the breaker's limit of 15A? Or is the 12A mower more powerful and able to push through the rough/thick patches on free current (without stalling)?
Should trip less or none.

The technical explanation is what limits the current through motor isn't the resistance of the windings (that's a dead short and will allow close to 100 amps), but back EMF created by rotor when it's spinning. If it slows down too much it loses that limit and getting closer and closer to short circuit, so more and more current is going through till it either burns or in your case trips the breaker. A 12A motor will have more torque while running and not slow down as much to lose that limit.
Deal Expert
User avatar
Feb 11, 2007
20287 posts
24036 upvotes
GTA
Elfwood wrote: Thanks. Yes that fits my observation of when the mower trips the breaker. So if I purchase a 12A mower, will it trip even more frequently (on rough/thick patches) since it's closer to the breaker's limit of 15A? Or is the 12A mower more powerful and able to push through the rough/thick patches on free current (without stalling)?
It could still trip if you let the mower bog down. With your current mower, you could try sharpening the blade and going slower over the tough patches. When you get your new mower, make sure the blade is sharp and avoid letting it bog down. Either slow down, or do more overlap (ie, run mower on 50% of last pass).
Our EV charges for 16+ hours at 12A on a 15A circuit with no issues, just to put your mind at ease. Of course, I can't run my 12A mower on the same circuit at the same time.

jzmtl wrote: Should trip less or none.
The technical explanation is what limits the current through motor isn't the resistance of the windings (that's a dead short and will allow close to 100 amps), but back EMF created by rotor when it's spinning. If it slows down too much it loses that limit and getting closer and closer to short circuit, so more and more current is going through till it either burns or in your case trips the breaker. A 12A motor will have more torque while running and not slow down as much to lose that limit.
+1
If the women don't find you handsome, they should at least find you handy.
Deal Expert
Jan 27, 2006
21157 posts
14702 upvotes
Vancouver, BC
Elfwood wrote: Thanks. Yes that fits my observation of when the mower trips the breaker. So if I purchase a 12A mower, will it trip even more frequently (on rough/thick patches) since it's closer to the breaker's limit of 15A? Or is the 12A mower more powerful and able to push through the rough/thick patches on free current (without stalling)?
In theory, less if not at all. The only reason a motor stops/slows when it hits a rough/thick patch is that it doesn't have enough momentum and power going into the patch to keep moving at the operational speed given the extra resistance from the patch. You probably noticed the motor change its tune when it hits a patch which usually signifies a change in speed. With a more powerful motor, to begin with, the motor probably has more momentum and speed going into the rough/thick patch as the motor would not have been slowed down as much by other grasses. In addition. the additional power of the motor moves things along over the rough/thick patch resulting in a smaller change in speed and a lower current draw as the motor won't stall or slow down as much. You will still probably hear a drop in speed in those rough patches but that drop won't be as bad as with an 8A motor.
Deal Expert
Jan 27, 2006
21157 posts
14702 upvotes
Vancouver, BC
engineered wrote: It could still trip if you let the mower bog down. With your current mower, you could try sharpening the blade and going slower over the tough patches. When you get your new mower, make sure the blade is sharp and avoid letting it bog down. Either slow down, or do more overlap (ie, run mower on 50% of last pass).
Our EV charges for 16+ hours at 12A on a 15A circuit with no issues, just to put your mind at ease. Of course, I can't run my 12A mower on the same circuit at the same time.
Yep. Anything one can do to reduce the resistance of the lawn will help the motor out. Another thing that works is doing two cuts, one at a slightly higher level than you want to remove the taller grasses and then one at the desired height. Alternatively, using a weed eater/line trimmer to 'pre-cut' the taller areas to a more reasonable height before using the lawn mower to cut to the desired height works well.