Kitchen Exhaust - 8 or 10 inch in lieu of 6 inch

Hi All!
We booked a new construction being built in Vaughan. I was wondering if it makes sense to increase the kitchen exhaust opening to 8 or 10 inch in lieu of the standard 6 inch hole from builder.

We do a lot of oily, spice cooking And 6 inch will definitely won’t do. Are there any 10 inch hole sizes range hoods for residential use or it’s only commercial applications only?
I will do 8 inch in any case.
35 replies
Sr. Member
Jan 19, 2013
708 posts
626 upvotes
Ottawa
Depends on CFM
Mostly seen 6" sometimes 7" on residential range hood.
Builder should be putting in some kind of makeup air system if your putting in a high cfm exhaust hood btw
Deal Expert
Aug 2, 2004
38384 posts
12008 upvotes
East Gwillimbury
If you plan to upgrade the range hood, definitely get an 8"

I regret not doing it. I am using an 8" to 6" duct and I doubt it is effective
Deal Addict
User avatar
May 18, 2004
2857 posts
507 upvotes
Ontario GTA
satin1410 wrote: Hi All!
We booked a new construction being built in Vaughan. I was wondering if it makes sense to increase the kitchen exhaust opening to 8 or 10 inch in lieu of the standard 6 inch hole from builder.

We do a lot of oily, spice cooking And 6 inch will definitely won’t do. Are there any 10 inch hole sizes range hoods for residential use or it’s only commercial applications only?
I will do 8 inch in any case.
depends on size of stove and fan you are getting.. 6 inch is standard.. 8 inch would be for very high cfm hoodfans and 10inch for the really big ones e.g. if you have a 36-48" stove
if you connect a fan to the lower size pipe it will get considerably more noisy.

one other thing to note, if you have a 30 inch stove, there are not a lot of fans that have high cfm for that size.
another thing to note is that if you truly get a high cfm fan, you will need a make up air otherwise you will run into issues.


lastly, when it comes to hoodfans, most people use them wrong. it's not about turning them on max after you already started cooking, you need to turn them on before you start to start the circulation.
secondly, depending on the type of burner depends a bit on what style fan, induction heat is different than gas.

lastly, there is no industry standard for how you should report the CFM, some may try to get a high as possible number by just showing what the motor can do, another may take into consideration the actual output after it's installed, e.g. with filters and a bend in the pipe and with equal motors those numbers will be very different.
Deal Addict
User avatar
May 28, 2009
1543 posts
529 upvotes
Ottawa
Gee wrote: If you plan to upgrade the range hood, definitely get an 8"

I regret not doing it. I am using an 8" to 6" duct and I doubt it is effective
many years ago we had a 4 " duct and bought a high CFM exhaust which needed 6". since it was winter we used a 6 to 4 converter or diffuser or reducer for a few months. this is an issue because it creates a blow back (more vol is trying to get out of a 4 " duct) and you could feel the air coming back into the house. you can go higher but shouldnt go lower.
Deal Fanatic
Nov 17, 2012
5379 posts
4994 upvotes
Toronto
I have an 8" duct servicing my Vent-a-Hood. It's a dual blower unit which pumps out 900 cfm if you believe them and it's 30 inches wide.

I got it used on eBay from the US back almost 10 years ago when I gutted our kitchen. $500 US shipped to Buffalo and CAD/USD were about on par at the time (0.98 or so). Has the dual blowers, lighting and heat lamps (the halogen bulbs in the photos have since been replaced with clear warming lamps).

IMHO the best option for serious venting and 8" duct is the minimum required. Mine is on an outside wall so there's a very short duct run.

003.JPG
005.JPG
004.JPG
Member
Apr 19, 2018
397 posts
124 upvotes
Scarborough
Always get an 8" vent duct for sure!
Don't worry be happy - Bob
Member
Apr 19, 2018
397 posts
124 upvotes
Scarborough
torontotim wrote: I have an 8" duct servicing my Vent-a-Hood. It's a dual blower unit which pumps out 900 cfm if you believe them and it's 30 inches wide.

I got it used on eBay from the US back almost 10 years ago when I gutted our kitchen. $500 US shipped to Buffalo and CAD/USD were about on par at the time (0.98 or so). Has the dual blowers, lighting and heat lamps (the halogen bulbs in the photos have since been replaced with clear warming lamps).

IMHO the best option for serious venting and 8" duct is the minimum required. Mine is on an outside wall so there's a very short duct run.


003.JPG005.JPG004.JPG
Not to hijack but how do you like you're vent-a-hood? Would you recommend it?
Don't worry be happy - Bob
Deal Addict
Sep 6, 2017
4615 posts
3080 upvotes
8" minimum but since you plan to do a lot of oily food I would go 10". You definitely don't want back pressure with the fan on max.
Deal Fanatic
Nov 17, 2012
5379 posts
4994 upvotes
Toronto
Prestonxavier wrote: Not to hijack but how do you like you're vent-a-hood? Would you recommend it?
I'd highly recommend them, but would have a hard time paying full retail for it.
Deal Expert
Aug 2, 2004
38384 posts
12008 upvotes
East Gwillimbury
torontotim wrote: I have an 8" duct servicing my Vent-a-Hood. It's a dual blower unit which pumps out 900 cfm if you believe them and it's 30 inches wide.
I have a Vent-A-Hood

Great unit. I just need an 8" exhaust
Last edited by Gee on Sep 10th, 2020 11:08 pm, edited 1 time in total.
Member
Apr 19, 2018
397 posts
124 upvotes
Scarborough
torontotim wrote: I'd highly recommend them, but would have a hard time paying full retail for it.
Is there significant mark-up on them? Wondering if i can negotiate the price with the retailer.
Don't worry be happy - Bob
Member
User avatar
Sep 25, 2003
284 posts
78 upvotes
Scarborough
Vent size selection will be dependent on the size of hood you plan to use and the volume of air you plan to move.

The roof cap on my 10” Vent is massive, about 27 x 20 inch in size and tbh looked a little silly on my house given its low roof line. But we have a 48” hood range and the manufacturer spec’d the vent size at 10”.
Deal Guru
Jul 7, 2017
10212 posts
5525 upvotes
SW corner of the cou…
I'm on my 2nd 2 motor Vent-a-Hood. First one came with the house when I bought it. Was impressed enough that I bought one for the house I am in now (came with a short-rise Faber downdraft which is powerful but so powerful it also sucks the gas flame away from the burner at lowest speed). 1st Vent-a-Hood only has a short run up and then 90 degrees and out. Current install has a 2' rise then a less than 90 degree turn running another 4-5' before another 90 degree turn and out through the roof.

Both work well so well I can make blackened foods indoors. Also have halogen lights while the old one only has a fluorescent tube and have warming lamps and a fold-away warming shelf. The only quibble I have is where the grease collects. On the VaH it collects on the grease collector just before the fan. Sort of a PITA to get up there to remove the grease trap and the wheel housing and wheels also get covered in grease. I have to take out the housing 2x a year to clean and the wheels once every 2 years.

I think the better design is where you have the grease traps somewhere before that. Makes cleaning easier and less grease might get up to the fan.

As for pricing you can always look in the used ads and also keep in touch with the distributor or dealer. I bought the current one I have at a distributor old demo close out (the model was obsolete, new model has non-replaceable LEDs in place of the GU-10 halogens I simply replaced with GU-10 LEDs) for quite a bit less than list (still expensive).

If anyone wants a 8" VaH roof exhaust jack for steeper roofs, I have a BNIB one for sale.
I smile when I see container ships sailing past my house laden with stuff made in China
Newbie
Mar 19, 2022
3 posts
3 upvotes
Remember that velocity is also important. Increasing duct size reduces velocity from the same blower. You want 25 fps for greasy air. 1500 fpm x .35 cu ft is 600 cfm in an 8 inch duct. You need to run about 1000 cfm to get that 25 fps velocity in a 10 inch duct. Match your duct size to your blower capacity. 10 inch duct likely needs 2 blowers, and if you run it to slow, you will line your duct with all the grease your baffle doesn't capture.
Deal Expert
User avatar
Mar 23, 2009
22529 posts
8938 upvotes
Toronto
Thread resurrection...

I'm thinking about getting a 36" ~600 cfm vent hood, but notice that most of them actually come with a 6" discharge duct, including higher end ones like Wolf.

I'm tempted to get a Bosch 500 series just because it has an 8" duct. What do you think? They're about $500 more than the competition (but likely much cheaper than the Wolf). I'm thinking that besides improved effectiveness, 8" may actually be quieter than 6" too.
Deal Guru
Jul 7, 2017
10212 posts
5525 upvotes
SW corner of the cou…
Quiet/noise level depends on the fan and placement. Some use a remote fan (separate from the hood) usually placed in the attic on some remote place. Could be a PITA to service/clean however. Even the undercabinet Faber fan is noisy. If you can, see them in action to experience noise levels.
I smile when I see container ships sailing past my house laden with stuff made in China
Deal Expert
User avatar
Mar 23, 2009
22529 posts
8938 upvotes
Toronto
thriftshopper wrote: Quiet/noise level depends on the fan and placement. Some use a remote fan (separate from the hood) usually placed in the attic on some remote place. Could be a PITA to service/clean however. Even the undercabinet Faber fan is noisy. If you can, see them in action to experience noise levels.
Unfortunately, a remote fan isn't going to be an option. As for seeing them in action, that's a problem, because most of the stores I've been to don't even have them on display, but when they do, they're usually not connected to power.

These are the Bosch models I'm considering:

https://www.bosch-home.ca/en/compare/sh ... HCP56652UC
Deal Guru
Jul 7, 2017
10212 posts
5525 upvotes
SW corner of the cou…
EugW wrote: Unfortunately, a remote fan isn't going to be an option. As for seeing them in action, that's a problem, because most of the stores I've been to don't even have them on display, but when they do, they're usually not connected to power.
Try the distributor. I bought my Vent-a-Hood from the local distributor who did have it hooked up in their showroom (so a demo unit that never ingested no cooking fumes).
I smile when I see container ships sailing past my house laden with stuff made in China
Deal Guru
Jul 7, 2017
10212 posts
5525 upvotes
SW corner of the cou…
I'm not in favour of those styles. The cooking vapours and going to rise with area increasing with height about cooking vessel (inverted cone). The hood is to contain these vapours (the deeper of the two would be better but both are not deep) with the fan serving to create a low pressure area where these vapours will hopefully head towards (i.e., not sucked out per se but create a low pressure area where gas will head towards).
I smile when I see container ships sailing past my house laden with stuff made in China