Duct Smoke Detector question

Hi, I am looking to put a duct smoke detector and was thinking of putting in the D4120... I am not entirely familiar with the wiring of a furnace and/or this sensor.. is it an installation that a avg person with some DIY skills can do? does anyone have experience with this (or another detector You would recommend) .. also given that this is a passive system.. anyone know how to test it to make sure it’s actually working.. any help will be appreciated... thanks
10 replies
Deal Expert
User avatar
Feb 11, 2007
22269 posts
27589 upvotes
GTA
Why a sensor in the ducts?
If the women don't find you handsome, they should at least find you handy.
Banned
Jun 4, 2020
1634 posts
1752 upvotes
Clarington, ON
My gut says you will need a power source separate from the furnace. The control voltage from the furnace would then be put through the NC portion of one of the form C contacts to cut power to the furnace when smoke is detected.

Testing - push the test button as described in the data sheet.


I will echo engineered - why?
Deal Addict
Oct 13, 2014
3203 posts
2598 upvotes
Just Moved To Somewh…
Is that finished basement being used as a separate residence? AFAIK - If not and it is just for your own dwelling then it is not required, specifically 9.10.18.5 addresses a single dwelling, however it also addresses a building that requires Fire Alarm System. Does your dwelling fit that requirement?

9.10.18.5. Smoke Detectors in Recirculating Air Handling Systems
(1) Except for a recirculating air system serving not more than one dwelling unit, where a fire alarm system is required to be installed, every recirculating air handling system shall be designed to prevent the circulation of smoke upon a signal from a duct-type smoke detector where such system supplies more than one suite on the same floor or serves more than 1 storey.

Refer to Sections 3.2.4.12 and 9.10.18.5 of OBC

https://www.ontario.ca/laws/regulation/120332

Now I could very well be misinterpreting the OBC and I will let others, more knowledgeable, comment.
#1 - “Don’t irritate old people. The older they get, the less “Life in prison” is a deterrent."
#2 - Are you a Sexual Intellect? /S - What you post in this thread may determine that.
Deal Expert
User avatar
Feb 11, 2007
22269 posts
27589 upvotes
GTA
BargainHunterCan wrote: It’s required by code for a legally finished basement..
OK, so it looks like it's designed to stop the HVAC from running if it detects smoke in the ducts. Hopefully it's required to be interlocked to the other smoke alarms as well.
If the women don't find you handsome, they should at least find you handy.
[OP]
Newbie
Aug 14, 2019
64 posts
11 upvotes
That’s correct, I need it as I am building a completely independent unit in the basement.

I am wondering if anyone can talk about any experience with wiring the sensor.. There are hardly any instructional videos on it online
Banned
Jun 4, 2020
1634 posts
1752 upvotes
Clarington, ON
BargainHunterCan wrote: That’s correct, I need it as I am building a completely independent unit in the basement.

I am wondering if anyone can talk about any experience with wiring the sensor.. There are hardly any instructional videos on it online
You say completely independant. I'm assuming this is not true and thst they are sharing hvac given your statement.


As per my above:
you will need a power source separate from the furnace. The control voltage from the furnace would then be put through the NC portion of one of the form C contacts to cut power to the furnace when smoke is detected.
[OP]
Newbie
Aug 14, 2019
64 posts
11 upvotes
That’s correct, I meant with a separate entrance etc.

For the separate power source.. are we talking about 120Vac or 24 Vdc?
Banned
Jun 4, 2020
1634 posts
1752 upvotes
Clarington, ON
BargainHunterCan wrote: That’s correct, I meant with a separate entrance etc.

For the separate power source.. are we talking about 120Vac or 24 Vdc?
Cut sheet for device you mentioned specifies it can be 24vac or 24vdc in terminals 9 and 10 ot 120vac to the specified terminals.

Edit: personally I would look at hardworking a 24vac transformer to your furnace shutoff switch to provide power to the detector.